Pipe Penetration UL Listing Number

Posted by  Markabout 6 years ago
Pipe Penetration UL Listing Number

Can you provide a UL number for the attached Pipe penetration detail using firestopping. 2 Hour Firerating using intrumescent Fire Stopping

vertical fire barrier,fire standards

1 Reply
Posted by Chase Hellanabout 6 years ago
Hilti Verified

Hello Mark,

I have attached one system - C-AJ-1155 which should work in both of your applications using FS-ONE MAX (intumescent firestop). C-AJ-1154 would also work for you if you do not exceed the annular space requirements.

The system your drawing has listed (C-AJ-1630) for the floor penetration would also work, however SIL GG and SIL SL are not intumescent.

https://www.hilti.com/firestops - you can use this link to search all of Hilti Firestop systems online.

Please let us know if you have anymore questions.

Thank you,
Chase