am looking for one side fire stop UL Systems for
head of wall joints & through penetration ( Metallic pipes, non metallic pipes, ducts & cable trays)
Hello,
It is going to depend on the type of wall/floor assembly being used along with the size of the penetrations.
Systems that provide a one sided installation include:
Joints - HW-D-0285, HW-D-0286, HW-D-0825.
Penetrations - W-L-1205, W-L-1206, W-L-2217, W-L-7068, W-L-7069, W-L-4011, W-J-1088, W-J-1089, W-J-4027, W-J-7038, W-J-7039.
You can search these systems through the HILTI Firestop Submittal Generator.
https://www.hilti.com/firestops
If these systems do not cover your application needs than you can submit an engineering judgement request form to usfirestopeng@hilti.com
I have attached a engineering judgement request form if needed.
Regards,
Dakota Reid