Anchor Bolts HAS E-55

Posted by Mamta Bhasinover 1 year ago
Anchor Bolts HAS E-55

Can hilti anchor bolts be modified in length by cutting off a top piece to make them shorter

adhesive,EPOXY,anchor bolt

1 Reply
Posted by Matthew Fordover 1 year ago
Hilti Verified

Hi Mamta, 

Hilti typically recommends against cutting anchors and engineers avoid cutting on anchors for the following reasons:

  • The mechanical properties of the anchor could be changed resulting in reduced load capacity.
  • The corrosion resistance properties of the anchor could be reduced during the cutting process.
  • Cutting could remove the length identification mark on the anchor (if applicable).
  • The threads of the anchor could be damaged.


These are only items to consider when cutting anchors and is not an exhaustive list. Final decision and design is ultimately at the discretion of the engineer on the project.

Hilti also offers cut-to-length anchor rods if a specific length is required for your application. For more information, please reach out to Hilti Customer Service at us-sales@hilti.com or 1-800-879-8000.

Regards,
Matthew

threaded rods,cut-to-length anchor rods