What post installed anchors are seismically rated for brick masonry?

Posted by Zachary Middleton10 months ago
What post installed anchors are seismically rated for brick masonry?

What post installed anchors are seismically rated for brick masonry?

anchor,post-installed

1 Reply
Posted by Craig Shaughnessy10 months ago
Hilti Verified

Hi Zach,

An anchoring solution that Hilti offers that is rated for seismic loading in multi-wythe brick and grout-filled masonry is the HIT-HY 270 adhesive anchor. Technical information can be referenced in Hilti’s Anchor Fastening Technical Guide on page 175. ESR-4143 for masonry and ESR-4144 for unreinforced masonry are also available on Hilti’s website. Please note that the suitableness of the HIT-HY 270 for an application such as this is ultimately at the discretion of the Engineer of Record (EOR) on the project.

If you have any further questions or concerns, please reach out to hnatechnicalservices@hilti.com.

Best,

Mia