Skip to main content
Cart

Using PROFIS with Custom Diameter Rods

Posted by JUAN SALASover 2 years ago
Using PROFIS with Custom Diameter Rods

Is there a way to account for a 2-1/4" diameter threaded rod (HAS-B-105 HDG) within PROFIS Engineering Anchoring-to-Concrete Module?

Hilit Profis,PROFIS anchor list

1 Reply
Posted by Ashley Couronover 2 years ago
Hilti Verified

Hi Juan,

The Anchoring-to-Concrete module within PROFIS Engineering does not account for any threaded rods with a diameter larger than 1-1/4" per the testing available in the respective ESR documentation for HIT-HY 200 V3 and HIT-RE 500 V3. However, Hilti has performed some additional testing with HTI-RE 500 V3 and larger diameter rods, including 2-1/4", which can be found in this technical bulletin.

Regards,
Ashley

Hilti HIT-RE 500 V3,Large Diameter anchor rods

1 comment on this reply
Posted by Jeff Morrisabout 1 month ago
Can you reshare the link? It no longer works.