Posted by ARSover 2 years ago
Using PROFIS to design anchor for masonry solid core.
Using PROFIS to design anchor for masonry solid core. Specified HY 200-A epoxy with A36 threaded rod. Why is there an error message about a limit of one (1) anchor per CMU core? Where is that specified in the Hilti literature/technical guide? Assuming this has to do with the structural integrity of the CMU after the hammer drilling?
1 Reply
Posted by Ashley Couronover 2 years ago
Hello,
If you are designing according to ASD, this information can be found in Hilti's Anchor Fastening Product Technical Guide on page 99 in Footnote 2 of Table 100. If you have any further questions, please feel free to email us at hnatechnicalservices@hilti.com.
Regards,
Ashley