Posted by Howard Young7 months ago
Using HY200-A V3
Hello. I am using threaded rod with the HY200-A adhesive anchor. The holes have been drilled all the way through the concrete slab (which it 5.5 inches). Could I still use the adhesive anchor?
Howard
1 Reply
Posted by Sinan Beskok7 months ago
Hi Howard,
Thank you for reaching out. Hilti does not have testing for through-bolted applications with adhesive anchor systems. Hilti’s published values do assume a minimum concrete thickness with sufficient concrete at the back of the hole. Consequently, use in a through-bolted application would be at the discretion of the Engineer of Record on the project.
For additional information, please reach out to hnatechnicalservices@hilti.com.
Kind regards,
Sinan