undersized penetrant

Posted by matt trullover 2 years ago
undersized penetrant

I am using hilti cast in sleeves and the penetrants are undersized for the sleeve. 2" penetrant in a 4"&6" sleeve, 4" penetrant in a 6" sleeve. is this acceptable, if not, what is the fix?

cast in sleeve,undersized penetrant

2 Replies
Posted by Tyler Thomasover 2 years ago
Hilti Verified

Hello,
What type of penetrant do you have - metallic or non-metallic wise? We have a few systems you can try to use- F-A-2103, F-A-1066, and F-A-1023. If none of them will work for your application, please advise what type of penetrant do you have and if an engineering judgment is possible, we can process one for you if you would like one.

Best regards,
Tyler Thomas
Senior Fire Protection Engineer
Hilti


Posted by LUKE JOYNERover 2 years ago

Submit your parameters to Engerineering. Might qualify under a System or EJ. Might need to do a F-A-2025