Posted by Wang Bo-Shiuan (Shawn)about 6 years ago
undercut inconsistent data
We found undercut 's minimum required concrete thickness is inconsistent between product specification and ICC-ESR report. For M12 HDA-PR, specification shows minimum concrete thickness 7.5in while ICC-ESR show 7.9in. Which one is correct? Please refer to attachment.
1 Reply
Posted by PARIS STANTONabout 6 years ago
Hi Shawn,
Sorry for the confusion, however, please use the values listed in the ICC-ES ESR. The Hilti technical data will be corrected in the next revision.
Regards,
Paris