Skip to main content
Cart

uncracked bond strength

Posted by Simon Deschambaultover 4 years ago
uncracked bond strength

For big diameter anchors, there is no characteristic bond strength in cracked concrete for threaded rod for RE-500

HIT 500,chemcial anchors

2 Replies
Posted by Ashley Couronover 4 years ago
Hilti Verified

Hi Simon,
 
The characteristic bond strength for larger diameter elements can be found in Table 2 of the 2019 Hilti Technical Supplement “Technical Data for Large Diameter Elements with Hilti HIT-RE 500 V3 Adhesive Anchor System” .
 
Regards,
Ashley


1 comment on this reply
Posted by Simon Deschambaultover 4 years ago
I know, but there is no value for CRACKED concrete.

Posted by Ashley Couronover 4 years ago

Hi Simon,
 
Unfortunately, Hilti did not perform additional testing in cracked concrete with larger diameter elements and HIT-RE 500 V3. You could use engineering judgement or on-site testing to account for variability in performance.
 
Regards,
Ashley