We have a 2 hour rated structural frame on a three story atrium. We need to attached cables for sway bracing of light fixtures. The only place we can attach the bracing is on an intumescent coated HSS 8x8 beam. We used UL Y634 as the design coating for the beam. Are we able to drill through the coating to install eyebolt's??
Hello Joseph, yes you are able to drill through the coating to install the eyebolts since these take up minor space on the HSS. If for any reason when drilling in the eyebolts in the intumescent is damaged, apply more product on the area to restore the required mil thickness. Finally, drilling through the intumescent will not affect the fire performance of Fire Finish 120 .Please let us know if you need more information.