UL System for firestopping Open End Conduit

Open end conduit penetrating 2hr barrier. Extends about 12" off the wall. Couldn't find a specific UL System for it. We found one where the conduit is allowed to be flushed or max 2" off the wall. We have some of them through gypsum board and some through cement block. Looking for solution , we can cut the sleeves down if needed and if no other option available. Conduits are blank , example attached.
Thanks in advance!

open end conduit,blank steel sleeve

3 Replies
Posted by Nathaniel Crawfordover 4 years ago
Hilti Verified

Hello Tomasz - thank you for using the AskHilti platform! We can address your condition with an Engineering Judgment which will be specific detail addressing your exact condition.

Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.)

Along with HCP, Hilti is excited to announce our new mobile app for all your firestop needs: Hilti Firestop Selector. Using the Firestop Selector app gives you easy access to the Hilti Fire Protection Design Team from the jobsite, on the road, or in the office to request a new EJ, an EJ Revision, or ask a Question anytime, anywhere. You can download the app on both the Google Play Store and the Apple App Store.

If you have any questions during the request process, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) or your local Hilti rep for assistance.


Best Regards,
Nate Crawford
Lead Fire Protection Engineer - Facade


Posted by Shara Castilloabout 3 years ago

what is the UL of the 2" max for open ended conduit you found. i have not been able to find it.
thank you.


Posted by Tomasz Rubajabout 3 years ago

didnt find one , need to apply for engineering judgement