Posted by Cameron Frostalmost 5 years ago
UL for Top of CMU
What UL would I use for Top of Rated CMU wall to concrete deck for CP606?
1 Reply
Posted by Michael Duncanalmost 5 years ago
Hello Cameron,
Thank you for your question regarding Hilti firestop. We have several UL listed systems for Head-of-Wall joints between CMU walls and concrete floors utilizing Hilti CP 606 Flexible Firestop Sealant. One example of these is HW-D-0268 (attached). If this system does not meet your needs, please feel free to browse our wide selection of firestop systems at hilti.com/firestops. You can filter through all of our tested systems by system type (joint or penetration), joint type (in this case head-of-wall), and more.
Please let us know if you have any additional questions.
Thank you,
Michael Duncan
Fire Protection Engineer
Hilti