Posted by Peter Longoriaabout 2 years ago
UL assembly - Steel beam penetrating 2 HR CMU
Hi, I'm looking for a UL assembly for a 2HR fire rated steel beam (W24) penetrating a 2HR 8" CMU shaft wall.
1 Reply
Posted by Nathaniel Crawfordabout 2 years ago
Hi Peter - WJ 7110 will be the closest system to your application. For your size beam, we will need to create an engineering judgment. You can submit for this using the guidelines below.
Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.)
Regards,
Nate Crawford - Lead FPE