Please see attached detail. What are your thoughts on this?
Hello,
It looks like this question may be a duplicate of another you have posted, so here is my response from the previous question. The attachment may be different but it did not come through here.
Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs.
This condition looks similar to HI/BP 120-04; however, we also have a couple of other alternative solutions (HI/BP 120-03 and HI/BP 120-05) that may work for you depending upon your installation sequencing.
If these systems do not work for you, we can address your application through an Engineering Judgment, which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.
Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.)
If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance.
Thank you,
Zach Rezazadeh
Fire Protection Engineer