Skip to main content
Cart

Two hour concrete floor Penetration for a 3'6 inches x1'8 inches

Posted by Danny Sejaover 2 years ago
Two hour concrete floor Penetration for a 3'6 inches x1'8 inches

At Huntington Pasadena Hospital, we have a project that requires a duct to start at ground level and penetrate
through 7 floors vertically without a fire damper. We need a 2-hour rated assembly to install around the duct at each floor

2 hour fire stop in floor,Hilti Firestop Products

1 Reply
Posted by Ricardo Mejiaover 2 years ago
Hilti Verified

Hello,

Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs.
Please see the attached UL listed system. If that does not meet your needs we can address your application through an Engineering Judgment which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.
To officially submit for Engineering Judgment please go to www.hilti.com/ej

Regards,
Ricardo Mejia