Top of wall fireproofing

Posted by Lee Ayersabout 5 years ago
Top of wall fireproofing

We have a cmu wall inside a precast double tee deck. The wall sits in between the web of two double tees, the outside of the wall sits too close to the web of one of the tees and does not allow the contractor to complete the top of wall nor install firecaulk at top of wall. Is there a detail where the side of the wall can be fire caulked to the side of the web? See attached pdfs 1 & 2.

fire stop confusion,Firestop at top of wall

1 Reply
Posted by Chase Hellanabout 5 years ago
Hilti Verified

Hello Lee,

There does not appear to be any UL listed systems for this application. However, with the details provided we should be able to create an engineering judgement (EJ) for the application.

Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/content/hilti/W1/US/en/engineering/design-centers/firestop/engineering-judgments.html

You can also submit any further questions here to the Fire Protection Design Team as well. Please do not hesitate to contact us know if you have anymore questions.

Thank you,
Chase
Fire Protection Engineer

firestop,EJ,Teedeck

1 comment on this reply
Posted by Lee Ayersabout 5 years ago
Thank you Chase. Please let me know if you need additional information.