Through penetration at a 2hr fire rated shaft wall but have access to caulk only one side

Posted by Shruthi Kasala Hemakumar11 months ago
Through penetration at a 2hr fire rated shaft wall but have access to caulk only one side

I have a steel conduit penetrating a 2hr fire rated shaft wall, I have access to caulk only one side of the wall and the steel conduit doesn't have a sleeve. Is there any UL detail or can an engineering judgement be provided for this condition where only one side caulking will suffice?

Through Penetration,Shaftwall,One Side Caulking,No Sleeve

1 Reply
Posted by Zachary Rezazadeh11 months ago
Hilti Verified

Hello,

Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs.

W-L1380 (see attached) may be an appropriate system for this condition; however, if this system does not address your condition, we can address your application through an Engineering Judgment, which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.

Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.)

If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance.

Thank you,

Zach Rezazadeh
Fire Protection Engineer