Posted by BRYAN COLLONSabout 3 years ago
The KB-TZ2 is not showing in Profis
The KB-TZ2 is not showing as an option in Profis. How can I load all anchor types in Profis
1 Reply
Posted by Ashley Couronabout 3 years ago
Hi Bryan,
Are you designing under seismic conditions? If so, do you have seismic type (a) selected? When seismic design is first selected in a new PROFIS Engineering file, the software defaults to the ACI 318-14 Section 17.2.3.4.3a provision for seismic tension design. If an anchor does not meet the ductility requirements of Section 17.2.3.4.3a, the anchor will be removed from the anchor selection menu within PROFIS Engineering. However, the anchor of interest may become available in the anchor selection menu when selecting one of the other seismic tension design provisions.
Regards,
Ashley