Stack concrete total thickness

Posted by Jesse Navarreteabout 4 years ago
Stack concrete total thickness

Given a 6" Concrete housekeeping Pad over a 6" Concrete Slab, can we assume 12" effective thickness for anchor design

anchor,concrete thickness,minimum embedment,total thickness

1 Reply
Posted by Emily about 4 years ago
Hilti Verified

Hi Jesse,

Hilti anchor testing is conducted in monolithic slabs only. Thus, Hilti does not have test data available for anchors installed in more than one layer of concrete. Engineering judgment could be considered if the housekeeping pad and supporting slab are sufficiently connected to act as one element. Additional information can be found in the American Concrete Institute (ACI) publication, “Anchoring into Housekeeping Pads,” which was originally published in the Q&A section of the December 2012 issue of Concrete International and can be purchased by clicking here to access the ACI online store. 

Best Regards,

Emily