We have a connection detail with a 1/2" diameter x 4 1/2" Hilti Kwik HUS-EZ Screw anchor and 3" min. embedment. The allowable shim stack is approximately 3/4". Due to field issues, they need to shim up to 2-3/4". Hilti Profis will not allow me to increase the shim stacks this high. Is there a mechanical anchor solution for the load and condition shown in the attached?
Paul Hopkins
paul.hopkins@tdhengineering.com
267-324-4830
Hi Paul,
You could use the anchor filter option within PROFIS Engineering to determine which anchor will work for your application based on the specific design parameters. If you would like to discuss your application further, please reach out to hnatechnicalservices@hilti.com or give us a call at 877-749-6337.
Regards,
Ashley