We are needing a detail for a head of wall shaftwall condition. The shaft is a 2hr shaftwall and there are voids between the high flute and the top track. Is there a detail to avoid getting into the shaft to complete the rating from the double layer side of this shaft? For example possible stuffing the gap then spray/caulking from outside the shaft?
Hello Matt,
Please see the attached listed firestop system HWD0750. It allows the joint at the head of the shaft wall to be stuff with mineral wool safing and sprayed with our CFS-SP WB Firestop Joint Spray from the finished side of the shaft. If this side is in-accessible or you would require another modification we can address the differences with an engineering judgement.
We are proud to announce the launch of the HILTI CONSTRUCTION PLATFORM (HCP), our company’s new engineering service website. This platform will be the home for all of your Fire Protection Design needs. Instead of emailing a PDF form for a request, the platform enables you to create new Engineering Judgment (EJ) requests, submit revisions to previously completed EJs or connect with an FPE on a question. HCP also enables you to track the status of your request.
You can find more information on how to access this new platform here: http://www.hilti.com/ej (US) or http://www.hilti.ca/ej (Canada.) If you have any questions or require assistance navigating the platform, please call Customer Service for help at 1-800-879-8000 (US) or 1-800-363-4458 (Canada.)
Along with HCP, Hilti is excited to announce our new mobile app for all your firestop needs: Hilti Firestop Selector. Using the Firestop Selector app gives you easy access to the Hilti Fire Protection Design Team from the jobsite, on the road, or in the office to request a new EJ, an EJ Revision, or a Question anytime, anywhere. You can download the app using the appropriate link below.
Hilti Firestop Selector App – Google Play Store
Hilti Firestop Selector App – Apple App Store