Seismic LBs loads for HDI-P TZ
I see pull out and Shear LBs values for the anchor. But i need to know what the ultimate Pryout rating in LBs is. That conforms to ASCE-7 and NFPA 13 requirements, either for 2016 and or 2019 edition.
1 Reply
Posted by Ashley Couronover 1 year ago
Hi James,
The HDI-P TZ does not have technical data specifically related to NFPA13, but Section 4.1.8.3 of ESR-4236 discusses seismic pryout strength in shear.
For more information related to seismic bracing, please see this article on Hilti's website. Additional technical information may be found in the Mechanical Anchors for Seismic Bracing technical supplement.
Regards,
Ashley