PROFIS showing 6.25-inch minimum thickness, but ICC and Hilti product technical guide says 6-inch depth is good. Is there a reason for the extra quarter inch showing on PROFIS?

Posted by Steele Albinoalmost 3 years ago
PROFIS showing 6.25-inch minimum thickness, but ICC and Hilti product technical guide says 6-inch depth is good. Is there a reason for the extra quarter inch showing on PROFIS?

I have a baseplate from a manufacturer that requires 1" bolts and a concrete pad that is 6" deep. The Hilti product technical guide and ICC say that 6" is good, but PROFIS is giving me an alert that the concrete pad needs to be at least 6.25" deep. Is there a reason that PROFIS is showing a larger number than the other two sources, or can I just adjust the depth in PROFIS and call it out in the project report?


Minimum emedment depth,Hiliti PROFIS Calculation Error

1 Reply
Posted by Ashley Couronalmost 3 years ago
Hilti Verified

Hi Steele,

The minimum concrete thickness requirement for HIT-HY 200 V3 can be determined from the equation shown in the attached image on page 57 of Hilti's Anchor Fastening Product Technical Guide. In order to better assist you, can you please confirm the embedment depth that you are using and email your ".pe" file to hnatechnicalservices@hilti.com.

Regards,
Ashley