Profis Masonry Design

Posted by Christopher D Kruse12 months ago
Profis Masonry Design

Hello: I'm trying to use Profis to design some masonry epoxy anchors in hollow block with sleeve. It appears the program is restricted to a limited sizes and embedment depths with HIT-HY 270. Please advise if there is way to use a larger anchor and depth say 5/8" or 3/4" with a sleeve.

HIT-HY 270,hollow CMU

1 Reply
Posted by Sinan Beskok12 months ago
Hilti Verified

Hello Christopher,

PROFIS Engineering pulls from Hilti’s published data for its calculations. For HIT-HY 270 in Hollow CMU following an ASD design method, this is from the Anchor Fastening Technical Guide. For an LRFD design method, ICC ESR-4143 is referenced. As such, installation conditions outside of the published test data and the Instructions for Use are unable to be modeled on PROFIS Engineering.

I hope this helps. If you have additional questions, please feel free to reach out to hnatechnicalservices@hilti.com.

Best,
Sinan

HIT-HY 270,profis engineering,hollow CMU,Screen Tube