Profis - Concrete Edge breakout - Fails at 10,00mm edge distance, passes at infinite edge distance?

Posted by Mike Mcraealmost 4 years ago
Profis - Concrete Edge breakout - Fails at 10,00mm edge distance, passes at infinite edge distance?

Trying to understand why this anchor arrangement fails when the edge distance is anything less than infinite. Surely it should pass if edge distance is extreme, like 10,000mm?

profis,Concrete edge distance

1 Reply
Posted by Emily almost 4 years ago
Hilti Verified

Hi Mike,

The PROFIS Engineering software is limited to a strict interpretation of the ACI 318-14 Chapter 17 anchoring-to-concrete provisions. Thus, the software is unable to determine on its own if a large edge distance should be considered finite or infinite. If an edge distance is defined in the software, PROFIS Engineering will evaluate the appropriate ACI 318-14 provisions accordingly. Whether or not to consider an edge distance large enough to be considered infinite is typically based on the engineer’s interpretation of the ACI 318-14 provisions. 

 For further technical assistance within North America, please contact hnatechnicalservices@hilti.com.

Cheers,
Emily