PROFIS - Anchor Depth Options Don't Match Website (TZ2)

Posted by CHASE GOODINGabout 2 years ago
PROFIS - Anchor Depth Options Don't Match Website (TZ2)

I ran a calculation in Profis that required expansion anchors. Looking at the TZ2 depth options in Profis, the deepest option is 4.75" for the 3/4" TZ2. Your website however lists 10" as your longest option. Why does Profis not match the options on the website? How can I calculate the capacities for these longer options?

For reference: https://www.hilti.com/c/CLS_FASTENER_7135/CLS_MECHANICAL_ANCHORS_7135/r8863215?CHA_GLOBAL_ANC_SIZE=3%2F4%20in&CHD_ANCHOR_LENGTH=10%20in&combo_content=77ebc4f63b7d57c901a6b3395737cee9&salespackquantity=10%20pc&itemCode=2210172

KB TZ2,Hilit Profis

1 Reply
Posted by Ashley Couronabout 2 years ago
Hilti Verified

Hi Chase,

PROFIS Engineering will analyze the anchor diameter based on the effective embedment depths that Hilti has testing for based on the technical information in ESR-4266. The KB-TZ2 is available within different lengths to account for various fixture thickness requirements which can be seen on pages 328-330 of Hilti's Anchor Fastening Product Technical Guide.

If you have further questions, please feel free to email us at hnatechnicalservices@hilti.com or give us a call at 877-749-6337.

Regards,
Ashley

Profis engineering software,KB-TZ2