I ran a calculation in Profis that required expansion anchors. Looking at the TZ2 depth options in Profis, the deepest option is 4.75" for the 3/4" TZ2. Your website however lists 10" as your longest option. Why does Profis not match the options on the website? How can I calculate the capacities for these longer options?
For reference: https://www.hilti.com/c/CLS_FASTENER_7135/CLS_MECHANICAL_ANCHORS_7135/r8863215?CHA_GLOBAL_ANC_SIZE=3%2F4%20in&CHD_ANCHOR_LENGTH=10%20in&combo_content=77ebc4f63b7d57c901a6b3395737cee9&salespackquantity=10%20pc&itemCode=2210172
Hi Chase,
PROFIS Engineering will analyze the anchor diameter based on the effective embedment depths that Hilti has testing for based on the technical information in ESR-4266. The KB-TZ2 is available within different lengths to account for various fixture thickness requirements which can be seen on pages 328-330 of Hilti's Anchor Fastening Product Technical Guide.
If you have further questions, please feel free to email us at hnatechnicalservices@hilti.com or give us a call at 877-749-6337.
Regards,
Ashley