Does profis allows anchor bolts with end plates instead of headed anchors?

Seismic Design,headed anchors

1 Reply
Posted by Sinan Beskok3 months ago
Hilti Verified

Hi Guillermo,

PROFIS Engineering does not currently include anchor bolts with end plates instead of headed anchors for cast-in-place calculations.

When using a hex head anchor, however, there is an option to add a small plate or washer to calculate concrete breakout in tension using a modified effective embedment found in the “Anchor“ tab (see below).


I hope this helps. If you have additional questions about PROFIS Engineering, please reach out to hnatechnicalservices@hilti.com.

Kind regards,
Sinan