Posted by Marcia Boltonalmost 4 years ago
Post installed reinforcement

I did not find an option for utilizing reinforcement that is embedded with Hilti epoxy. I only saw options for Hilti steel rods. Does Hilti profis calculate capacities for this and if yes, how do I execute that option?

Post installed reinforcement,Anchor epoxy

2 Replies
Posted by Emily almost 4 years ago
Hilti Verified

Hi Marcia,

If the design's anchor plate design approach is set to CBFEM, the software will filter out rebar as an anchor element option. Changing the baseplate design method to Rigid will allow you to select adhesive with rebar. See the screenshot below to see where to change your anchor plate settings.

Regards,
Emily

REbar,CBFEM,Rigid

Posted by Emily almost 4 years ago
Hilti Verified

Screenshot attached