POST INSTALLED ANCHORS IN 6 INCH CMU

Posted by  MPhungalmost 3 years ago
POST INSTALLED ANCHORS IN 6 INCH CMU

I do not see any data in your ICC report for post installed anchors in 6" cmu. Can you please direct me as to where I can find some values.

CMU,post installed

1 Reply
Posted by Ashley Couronalmost 3 years ago
Hilti Verified

Hello,


Hilti has not performed testing with our masonry anchors into 6-inch CMU blocks. However, the engineer may consider making the judgement when designing with Hilti masonry products, such as HIT-HY 200 or HIT-HY 270 into fully grouted CMU, that the values published based on an 8-inch block may be used provided that the maximum depth is limited to 4” since AC58 limits this for 8-inch blocks.

Ultimately, it is the responsibility of the Engineer of Record to make the judgment and onsite testing may be considered to validate the judgment.


Regards,
Ashley


cmu size