Posted by Ibro Vehabovicover 2 years ago
Post-Installed Anchors Bigger than 1.25 inch

Any plan for adding post-installed anchors bigger than 1.25 inch to your PROFIS
ENGINEERING software?

post-installed,ANCHORS,Bigger

2 Replies
Posted by Ashley Couronover 2 years ago
Hilti Verified

Hi Ibro,

There are no plans at this time, but it will be taken under consideration. In the meantime, please refer to this technical bulletin for HIT-RE 500 V3 with large diameter elements.

Regards,
Ashley

Hilti HIT-RE 500 V3

1 comment on this reply
Posted by Ibro Vehabovicover 2 years ago
Thank you much Ashley. Why 1.75 inch diameter is not included in this Technical Bulletin?

Posted by Ashley Couronover 2 years ago

Hi Ibro,

The additional testing was done only for the diameters listed in the technical bulletin. If you would like to use a different diameter, the decision will be up to your engineering judgement and/or on-site testing.

Regards,
Ashley