Posted by Dan Blumbergabout 3 years ago
Post Installed Anchor Bolts

We need to post install 4x 3/4" anchor bolts to replace 4 anchor bolts that were damaged. I have read previous articles which stated that Hilti recommends staying 3-1/2" back from edge of concrete. Please confirm that this is still correct. We also need to confirm that the new anchor bolts are acceptable to be epoxied in within 1 1/2" of the damaged ones.

Please confirm.

anchor bolt,Post installed Anchor Bolt.

1 Reply
Posted by Danielle Filerabout 3 years ago
Hilti Verified

Hi Dan,

Please refer to the answer from this previous question here. As far as the edge distance concerns, it will depend on the type and size of anchor. The minimum edge distance requirements can be found in the technical information for whatever adhesive you choose. If you need additional assistance, please reach out to one of Hilti's engineers at 877-749-6337 or hnatechnicalservices@hilti.com.

Regards,
Dani

Edge Distance,abandoned anchor