Posted by  Fritoabout 5 years ago
Pipe insulation in a W-L 1001 wall

I cant find the detail of a w-l 1001 wall penetration. We have a 1 hr wall (u465) with 1/2 inch copper plumbing lines penetrating with 1/2 fiberglass insulation. Can we fire caulk around the insulation or does the fire caulk have to be around the copper since fiberglass can melt?

W-L 1001 insulation,pipe insulation

1 Reply
Posted by Raymondabout 5 years ago
Hilti Verified

Greetings Frito. Thank you for checking out ASK Hilti! Please utilize WL5029 to accommodate the application you describe in your inquiry.

Under fire conditions, Hilti FS-One Max Intumescent Firestop sealant will activate and intumes through the pipe insulation effectively closing off the opening.

Thank You for choosing Hilti as your Firestop Experts!

Best Regards,

Raymond Prescott V,
Fire Protection Engineering Team