Posted by KYLE KIMover 2 years ago
Per ACI, stand off check is not required. Is there anyway to input grout without stand off check?
Per ACI 318-19, I don't see any requirement for stand off check (lever arm). But ACI 318-19 CH 17.7.1.2.1 requires Vsa shall be multiplied by 0.8 when anchors are used with built-up grout pad. Can 0.8 factor be applied without stand off check?
1 Reply
Posted by Danielle Filerover 2 years ago
Hi Kyle,
Please see the answers/discussion from this previous question. Unfortunately, it is not possible to turn off the ETAG provisions for steel lever arm failure.
Regards,
Dani