One side access UL firestop system

Posted by JEREMIAH PELOWSKIover 2 years ago
One side access UL firestop system

Im looking for a UL firestop system uninsulated 18x12 galv steel duct penetration through steel framed gypsum wall with only one side access

One sided application.,penetation,gypsum wall assembly

1 Reply
Posted by Jaeger Coxover 2 years ago
Hilti Verified

Hello,


Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs. Please see attached for Hilti ul/cul classified system W-L-7319.


If this system will not meet your exact application needs, we can address your application through an Engineering Judgment which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.


To officially submit for Engineering Judgment please go to www.hilti.com/ej


Regards,



Jaeger Cox