We're moving some old cantilever racks from our West Sacramento location to our new building in Rocklin, CA..
The county is asking for an engineered anchor design to meet current standards ACI 355.2 and ICC-ES AC193.
I'm no engineer! I muddled around your PROFIS software a bit, but quickly realized that it's way above my pay
scale. Will you help me?
Hi Dave,
Unfortunately, Hilti is unable to offer registered design services due to liability reasons. However, I can provide you with some resources to assist you. For information on the Hilti anchors that have approvals per ACI 355.2 and AC193, please refer to the Anchor Selection Guide on page 7 of Hilti's Anchor Fastening Product Technical Guide. Additionally, below are some technical resources for designing with anchors in PROFIS Engineering:
- Hilti has several how-to videos to help users get started with the PROFIS Engineering Suite software. For additional information on the various design modules/methods, Hilti provides several on-demand Ask Hilti webinars on topics such as base plate design, anchoring to masonry, and anchoring to concrete-over-metal deck.
- For further information on the software's functions and its calculations, see this PROFIS Engineering Design Guide.
- PROFIS Engineering FAQ on Ask Hilti
Regards,
Ashley