Minimum effective embedment detph

Posted by Kenneth Chowover 6 years ago
Minimum effective embedment detph

Is it possible to use an anchor less than the minimum embedment depth?

A contractor wants to use a larger S.S. using Hilti HY-200 from 1/2" to 3/4". The original effective specified embed depth is 75mm. The depth of concrete is only 5". Strength-wise, the 1/2" rod works comfortably, is there any issues with upsizing the rod? The effective embedment is less than the minimum as originally noted in the design guides.

minimum thickness,minimum embedment depth

1 Reply
Posted by PARIS STANTONover 6 years ago
Hilti Verified

Hi Kenneth,

Per ACI 318-14 Section 17.3.2.3, post-installed adhesive anchors are limited to a minimum effective embedment depth (hef) of 4da and a maximum effective embedment depth (hef) of 20da. For effective embedment depths lower or higher, the engineer on the project would need to consider using engineering judgment or on-site evaluation to account for potential variability in performance.

Regards,
Paris

minimum embedment depth