Skip to main content
Cart

Min edge distance for expansion anchors

Posted by Yuting Ciover 3 years ago
Min edge distance for expansion anchors

I have contractor installed expansion anchors only 1.5'' away from concrete slab edge. Is this acceptable? ESR-1917 report recommends min. 3'' edge distance for 5/8'' dia anchors

Field Condition,Misplaced Anchors

1 Reply
Posted by Emily over 3 years ago
Hilti Verified

Hi Yuting,

For a 5/8" carbon steel Kwik Bolt TZ, the smallest minimum edge distance is 3.25" as per Table 3 in ESR-1917. Installing at a smaller edge distance is out of the scope of testing. Installing too close to the edge of concrete may result in spalling or cracking of the concrete upon installation.

Regards,
Emily

Edge Distance,Kwik Bolt TZ,ESR-1917,edge of concrete