WL-1410 is for flex or conduit penetrating through one side of a wall. Is there a similar UL for mc cable ?
Hello,
Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs.
W-L-3310 is a UL/cUL classified Hilti listed system showing a membrane penetration for up to 3 metal clad cables in the same opening. I have attached this system here. If this system does not meet your needs, we can address your application through an Engineering Judgment, which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.
Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.)