Masonry Anchorage installed in end-of-wall or vertical members of wall openings

Posted by Wover 2 years ago
Masonry Anchorage installed in end-of-wall or vertical members of wall openings

In previous technical guides for masonry anchorage, specifically the KWIK HUS-EZ fasteners, you supplied a table 33 which gave the allowable loads installed in end-of-wall or vertical members of wall openings. Is this something that is being tested or are there still capacities for these anchors to be installed in end-of-wall conditions and where might one find that information in the new masonry anchor design guide 2023 that was published that discusses the changes to AC58?

Masonry Design,Masonry anchors

3 Replies
Posted by Ashley Couronover 2 years ago
Hilti Verified

Hello,

The width of a typical CMU block is 7-5/8”. For installation into the face of grout-filled CMU, the minimum edge distances for the KH-EZ installed into the face of grout-filled CMU is 4”. Therefore, if you installed an anchor directly into the middle of the block, the minimum edge distance requirements would be violated. Since these edge distances are violated, there is no testing for side of wall applications. Technical information related to our LRFD data for masonry can be found in the Masonry Design Guide.

Regards,
Ashley

Masonry Design,LRFD masonry

1 comment on this reply
Posted by Laura Barbero-Buffaover 2 years ago
What if the block is 12 CMU? that would meet the requirement of the edge distance. How do you recommend I design such a connection? The software using ASD doesn't allow for 12 block and only allows for one anchor in an end of wall condition. Thanks!

Posted by Matthew Fordover 2 years ago
Hilti Verified

Hi Laura,

Hilti's supportive testing is based on CMU units conforming to ASTM C90 with a nominal size of 8" x 8" x 16". For CMU units with different dimensions, it will be up to engineering judgement to evaluate anchor performance.

For additional assistance, please reach out to hnatechnicalservices@hilti.com or give us a call at 877-749-6337.

Regards,
Matthew

cmu size

1 comment on this reply
Posted by Wover 2 years ago
Hilti Profis Engineering allows for LRFD design of Masonry fasteners into 12 in CMU units, albeit only into the face or top of wall conditions. Seeing as Hilti previously had test data for end-of-wall connections as recently as the Anchor Fastening Technical Guide, Edition 22, and seeing as Simpson Strong-Tie has end-of-wall data with ICC ESR test report validation, does Hilti have any idea when end-of-wall will be available for their Hilti KH-EZ anchors?

Posted by Matthew Fordover 2 years ago
Hilti Verified

Hello,

Unfortunately, the availability of data for the KH-EZ installed into the end of grout-filled CMU walls is unknown.

Regards,
Matthew

grouted CMU