I want to use Hilti chemical anchor products to install equipment in the factory. The manufacturer of the equipment provided M24 bolts and nuts, and the required installation torque is 350 Nm. Could you please let me know which of your chemical products I should use and what the required drill hole depth and diameter should be to meet these conditions?
(Concrete foundation is 4000PSI)
Hi Brian,
Unfortunately, Hilti does not have any adhesive anchoring systems with a maximum installation torque value above 200 ft-lb. If the maximum torque value is exceeded, then anchor performance could be affected. Also, embedment depth and nominal anchor diameter will ultimately be specified by the Engineer of Record on the project.
For additional assistance, please reach out to hnatechnicalservices@hilti.com or give us a call at 877-749-6337.
Regards,
Matthew