M24 Chemical anchor Drill hole depth and diameter requirment to meet installation torque of 350Nm

Posted by Brian Kimabout 2 years ago
M24 Chemical anchor Drill hole depth and diameter requirment to meet installation torque of 350Nm

I want to use Hilti chemical anchor products to install equipment in the factory. The manufacturer of the equipment provided M24 bolts and nuts, and the required installation torque is 350 Nm. Could you please let me know which of your chemical products I should use and what the required drill hole depth and diameter should be to meet these conditions?
(Concrete foundation is 4000PSI)

Embedment Depth,Chemical Anchoring for Concrete,installation torque

1 Reply
Posted by Matthew Fordabout 2 years ago
Hilti Verified

Hi Brian,

Unfortunately, Hilti does not have any adhesive anchoring systems with a maximum installation torque value above 200 ft-lb. If the maximum torque value is exceeded, then anchor performance could be affected. Also, embedment depth and nominal anchor diameter will ultimately be specified by the Engineer of Record on the project.

For additional assistance, please reach out to hnatechnicalservices@hilti.com or give us a call at 877-749-6337.

Regards,
Matthew

adhesive anchoring system