Lower MAsonry compressive strength

Posted by WTSabout 3 years ago
Lower MAsonry compressive strength

I have a customer who wants to use the Titen HD post drill anchor to a grout filled masonry unit during erection. That being said, the grout compressive strength during intermediate period is lower than what the ESR requires. ESR requires a minimum of 1500 psi for masonry compressive strength. On the free version of the HILTI profis that I am using, there is no option to adjust the masonry compressive strength. If I purchase the premium version, do you have this option to adjust the Masonry Compressive Strength (F'm) to get the desired value?

Lower Masonry compressive strength,intermediate period

1 Reply
Posted by Ashley Couronabout 3 years ago
Hilti Verified

Hello,


You are unable to adjust the compressive strength of the grout within PROFIS Engineering. If you are installing an anchor with grout that has a compressive strength that is outside the scope of Hilti’s testing, the decision would be up to the engineering judgement of the Engineer of Record or on-site testing to account for variability in performance.


Please note, the Titen HD is not a Hilti anchor. A Hilti screw anchor option to consider would be the KH-EZ.


Regards,

Ashley

Profis engineering software