Looking for a detail for line set penetrations

Posted by David Lockwoodover 1 year ago
Looking for a detail for line set penetrations

I have this detail that states only 2 Tstat wires can pass through a ceiling penetration. Because the linesets follow the tstat line this means that I can only have two line sets / tstat lines penetrate through ceilings. Is there a detail out there that allows more penetrations through a ceiling in this case?

Hvac,Linesets,tstat wires

1 Reply
Posted by JESSICA STARKSover 1 year ago
Hilti Verified

David,

Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs. You are correct that you are limited to two thermostat wires, which ultimately would limit you to two line sets. As such, we do not have a system that matches your parameters for more than two wires at this time; however, we can address your application through an Engineering Judgment, which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.
 
Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.) 
 
Along with HCP, Hilti is excited to announce our new mobile app for all your firestop needs: Hilti Firestop Selector. Using the Firestop Selector app gives you easy access to the Hilti Fire Protection Design Team from the jobsite, on the road, or in the office to request a new EJ, an EJ Revision, or ask a Question anytime, anywhere.
 
If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance.

Thank you,

Jessica Starks
Senior Fire Protection Engineer