Posted by Neerja Puniyaabout 4 years ago
Load application

I have been provided anchor loads by pump base supplier, Can I put loads for each Anchor in Profis software?

Pump base,anchor loads

1 Reply
Posted by Emily about 4 years ago
Hilti Verified

Hi Neerja,

If you are evaluating a group of anchors in a single design, the combination of shear forces, tension force, and moments applies to the entire group of anchors and forces cannot be isolated and applied to a single anchor within a group of anchors. In other words, the load combinations apply to all anchors in the design. For more information on how PROIFS Engineering analyzes load combinations, please see the PROFIS Engineering Design Guide here.

Cheers,
Emily