Large Diameter Post-Installed Epoxy Anchors Not Available in Hilti PROFIS

Posted by MARK KOSKY6 months ago
Large Diameter Post-Installed Epoxy Anchors Not Available in Hilti PROFIS

Large diameter (1.5" and 1.75" diameter) cast-in-place anchors with an approximately 24" embedment were installed in the wrong locations. Can Hilti provide technical documentation or design information regarding the use of HIT-HY 200 V3 and/or HIT-RE 500 V3 for large diameter anchors (1.5" and 1.75" diameter)? Hilti PROFIS only allows up to 1.25" diameter anchors for use with these epoxies.

large diameter,epoxy anchor

1 Reply
Posted by Mia Brownell6 months ago
Hilti Verified

Hi Mark,

Hilti has performed limited additional testing with HIT-RE 500 V3 and large diameter elements. Please see this technical bulletin here for more information. Hilti has not performed testing with HIT-HY 200 V3 adhesive and threaded rods larger than 1-1/4" in diameter.

If you have any further questions, please reach out to hnatechnicalservices@hilti.com.

Best,

Mia

adhesive anchor,large diameter elements