Skip to main content
Cart

Large Diameter Anchor Bolts in PROFIS

Posted by Aaron Thomasover 2 years ago
Large Diameter Anchor Bolts in PROFIS

I'm working on a bridge project with large loads. Why is PROFIS limited to 1 1/4" diameter adessive anchor bolts and larger bolts can not be used? Is there a setting I am missing?

large diameter,adessive anchors

1 Reply
Posted by Ashley Couronover 2 years ago
Hilti Verified

Hi Aaron,

The largest diameter of threaded rod that is available within PROFIS Engineering is 1-1/4" due to testing within the ESR documents for the respective anchor. If you are going to be using the HIT-RE 500 V3, Hilti has done some additional testing with a larger diameter threaded rod. The testing can be found in this technical bulletin.

Regards,
Ashley

large diameter elements