Posted by NICOLE THOMPSONover 2 years ago
Kwik TZ2 wedge anchor cure time

Does the 21day concrete set time apply also with post-install anchors that do you rely on the chemical epoxy bond? Is there any table of reductions in concrete strength and an absolute minimum day length prior to installing a wedge anchor like the Kwik TZ2?

anchor,cure,Wedge,time

1 Reply
Posted by Ashley Couronover 2 years ago
Hilti Verified

Hi Nicole,

It is recommended that mechanical anchors not be placed/installed in concrete cured for less than 7 days. This can be seen on page 10 of Hilti’s Anchor Fastening Product Technical Guide.

Regards,
Ashley