KWIK HUS-EZ Minimum Edge Distance in CMU

Posted by Linda Petersover 2 years ago
KWIK HUS-EZ Minimum Edge Distance in CMU

The minimum edge distance for the KWIK HUS-EZ is 4" in CMU. Does this mean that these anchors cannot be used in the side wall of an 8" CMU wall since the wall is actually 7 5/8" wide? I'm looking for a post installed connection into the end of a wall and would prefer to connect directly to the end wall as other connections will become much most complicated and costly.

Kwik-Bolts,bolt edge distance,8 CMU

1 Reply
Posted by Ashley Couronover 2 years ago
Hilti Verified

Hi Linda, 

The minimum edge distance values for the installation of the Kwik HUS-EZ mechanical anchor into the side of a CMU wall can be found in the snippet of Table 33 below from the Anchor Fastening Technical Guide. Figure 7 from the technical guide references the different anchor locations in end of wall or wall opening applications. 

Regards,
Ashley