For a 1/2" KB TZ2 Anchor with 2-1/2" effective embedment, the minimum concrete thickness is stated as 5".
For a concrete deck, the requirement is to keep the hole minimum 5/8" from the surface.
If an anchor is installed from the top into a deck which is 4-1/2" thick in addition to 3" steel deck (total 7-1/2") can the 2-1/2" eff. embedment be used given the hole would be 5/8" from the steel deck and there is a steel deck/flute providing additional cover?
Hi Natik,
Installations of the KB-TZ2 into the top of concrete over metal deck must be in compliance with Table 9 and Figure 5D of ESR-4266 to fall within Hilti's scope of testing. Unfortunately, the largest tested effective embedment depth into the top of concrete over metal deck is 2".
For additional assistance, please reach out to hnatechnicalservices@hilti.com or give us a call at 877-749-6337.