Posted by Brent Cunninghamalmost 3 years ago
KB-TZ in concrete slab calc

I'm working on a legacy project using KB-TZ's and need to calc an anchor. Is there an option in the software to calc a KB-TZ in a concrete slab? I specified a 1/2" x 3 1/4" embed but the contractor only got 3" embed so I want to show a 2 1/2" embed works.

HILTI KB-TZ,Calculation explanation

1 Reply
Posted by Danielle Fileralmost 3 years ago
Hilti Verified

Hi Brent,

To avoid confusion and engineers specifying outdated anchors, Hilti removes old anchors and only keeps the current anchor portfolio in PROFIS Engineering. Unfortunately, there is not a way to design legacy anchors in PROFIS Engineering at this time. Please feel free to reach out to Hilti's engineering team at hnatechnicalservices@hilti.com if you need old technical data to perform calculations.

Regards,
Dani